The amount of heat energy lost from a
house will depend on a number of things:
If it is very cold outside and very hot
inside more heat energy will be lost than if there is only a small difference.
Of course, if the temperature outside is the same as the temperature
inside then no heat energy will be lost at all!
So the amount of heat energy
lost will depend on the TEMPERATURE DIFFERENCE.
If we double the area of a wall
then we double the amount of heat energy, passing through the wall at
any time.
So the heat energy lost will depend on the AREA,
The amount of energy lost will
depend on what the surfaces are made of and how thick they are. So that
we can work out heat losses from houses, tables of values are given
for different building materials. These are called U VALUES.
The U value tells you how much heat energy will pass through a 1 m2 piece of the
material in 1 second if there is a 1°C temperature difference between
the two sides of the material.
Here are some U-Values for building materials:
BUILDING MATERIAL
|
U-Value / (W m-2
oC-1)
|
Roof
Uninsulated roof
Insulated room
Wall
Cavity wall
Cavity filled wall
Floor
without carpets
with carpets
|
2.0
1.0
1.0
0.5
1.0
0.3
|
Windows and doors:
Single glazed
Double glazed
|
5.0
2.5
|
EXAMPLE: Calculatie
the heat energy lost per second from a poorly insulated house when the temperature inside the house is maintained at 18oC by the central heating system and the temperature outside is only 2oC.
The dimensions are as follows:
- area of uninsulated
roof =150 m2
- area of walls = 300
m2
- area of single-glazed
windows and doors = 50 m2
- floor area (uncarpeted)
= 150 m2
Temperature difference
(DT)
= temperature inside - temperature outside
= 18 - 2 = 16°C
Heat energy lost per second = U-value
(W/m2°C) x area (m2) x DT
(°C)
Heat energy lost per second
through:
the roof = 2 x 150 x 16 = 4800 W
the walls = 1 x 300 x 16 = 4800 W
the windows and doors = 5 x 50 x 16 = 4000 W
the floor = 1 x 150 x 16 = 2400 W
Total heat energy lost per second through
the whole house
= 4800 + 4800 + 4000+ 2400
= 16000 W
= 16 kW
Therefore to keep the house 16°C warmer
than the outside would require a constant 16 kW output from the heating system.
-------------------------------------------------------------------
Q1. Use the table of U values above to calculate
the heat energy lost per second through a 1m2 single glazed
window.
a) when the temperature outside is 0°C
and inside is 20°C.
b) when the temperature outside is 10°C
and inside is 20°C.
Q2. Use the table of U-values to calculate
the heat energy lost per second from this well insulated house when the temperature difference =
(temperature inside - temperature outside) = 18 - 2 = 16OC .
- area of insulated
roof = 150 m2
- area of cavity
filled walls = 300
m2
- area of double-glazed
windows and doors = 50 m2
- floor area (carpeted)
= 150 m2
|